Just been to price up for some new kitchen lighting. I knew in advance that there was no cpc on the lighting circuit.

Had a quick look at the board, recently done 17th board, all nicely labelled and warning of no cpc on lighting circuit. Looked inside, found the cable, twin sheathed no earth.

Had a look at his EIC, all properly filled in etc except for the lighting circuit.

r1r2 - no entry (expected)

Insulation L to N - >200M

Insulation L to E - >200M (well it would be if there was no earth ;) )

Zs - 0.63 ???? :| ?:| ? :| Where did he take that from, then?

 
Parallel path? But seems very low for that.

Bathroom light bonded?

Shouldn't really be filled in though, even if he did get a reading its a bit of a false statement calling it Zs.

 
I recently connected a boiler and noticed a nice new 17th edition C/U. Great i thought, no M.E.B`s to install. Looked inside the C/U and there was only a 6mm

 