hello chaps,
how many mwc would you give for changing 11 pendants? 1 per room or 1 per circuit?
how many mwc would you give for changing 11 pendants? 1 per room or 1 per circuit?
No problem Ped, any time. All this paperwork stuff gets up my nose, so do as little as possible.thanks Deke
i have some vinyl labels what i stick on consumer units / alarm panels etc for stuff like this. much less likely to get lost/thrown awayyeah well, they are moving so wanted new owner to have all the certs, alpng with the cards i droped all over the place lol
Since we are being pedantic here, that's not quite right. You should still test every fitting but only issue one cert per circuit with the highest readings recorded.Its the circuit you test not each fitting per circuit, so like its been said just 1 cert per circuit, every cert would have the same characteristics if done for each fitting..