Dear me... all this talk about "extraneous conductive part" ???
The armour of a cable is there for TWO reasons; 1, to be used as a CPC, and 2, To protect those that may damage the cable from electric shock.
It is NOT NOT NOT just there to provide mechanical protection, it is to provide shock protection to those that might damage the cable too, which is why you have to use armoured cable or an EARTHED metal plate if a cable is less than 2" deep in a wall..
You cannot earth the armour ONLY at the load end because you think it is merely an extraneous part, it is not, as i said, it is an integral part of the electrical protection of the cable and therefore must be earthed at the supply end.
Disagree??, ok, what if someone was to spike the cable near the supply end??? You have gone and doubled the length of the earth fault loop. What about ADS?? what about EFLI?? How is the supply going to disconnect in the required time???
What if a cable is disused [say pot ended] or someone decides to TT wherever it is going??? or disconnects the "earth" to the armour for any other reason. You now have a cable with no shock protection for those that may damage it..
If you are going to do that you might as well have used twin and earth...
john..