how to calculate power( wattage) on 3 phase

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
Hi, Just thought i would expand on that a bit.

It would be; Line voltage [400v] x the current [in one phase] x square root of three [1.732]

All this assumes a "balanced load" I.E. all three phases are carrying the same current.

OR

Phase voltage [230v] x current [in one phase] x 3

If you did it this way, i am not sure of the effect of an unbalanced load, although i am sure other forum members will be able to assist you with this [bit beyond me!]

Anyway, the answer would be in KW.

If you wanted KVA you would have to multiply the result by [PF x Efficiency]

john..

 
Hi Sidewinder, that is what i said, [i think]

"Anyway, the answer would be in KW.

If you wanted KVA you would have to multiply the result by [PF x Efficiency]"

Well, ok, i should have left out the bit about efficiency!

john..

 
Apprentice, its the letters, kW is not the same as KW,

Likewise, kVA is not KVA , there is difference , just the same as r1 or R1.

That is what Sidewinder means,I think.

 
Hi all!

I think what you mean is, that as i was referring to quantities measured in "thousands" [of watts] the correct prefix would [should] have been a lower case "k" [to denote "kilo" as in 1000] and not an upper case "K" that denotes a different quantity!! [1024]

Sort of [but not quite] along the same lines as mW are most very certainly not the same as MW!!!!!!

I have to say, i think this forum is brilliant!! Best one by far!!

John..

 