In loft contactor for shower

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

GeoffRC

New member
Joined
Mar 16, 2016
Messages
3
Reaction score
0
Location
Saltash
I have a 10.8kw shower with a 50Amp ceiling switch which is bulky and unsightly is there any way i can fit a 50/60amp contactor in the loft enabling me to have a a smaller switch in the ceiling 

 
Is there an actual requirement to fit a ceiling (or similar) switch, bearing in mind that a 60898 MCB is a qualifying isolation device?

 
Thought of that binky but there is a joist right above switch position 

And for you Lusk the answer is I don't know but don't want power onto the shower all the time

 
Is there an actual requirement to fit a ceiling (or similar) switch, bearing in mind that a 60898 MCB is a qualifying isolation device?
This would be mostly down to the manufactures instructions, which for a long time have generally said a double pole isolating switch with contact gaps min 3.0mm separation, or similar wording, must be installed. a 60898 would not provide this. 

Doc H

 
Pick any make or model you like do a quick search for installation instructions see what they say. e.g. Mira Sport 9.0kw give us. http://www.mirashowers.co.uk/onlinecatalog/pdf/1175283_w2_d_mira_sport_iug.pdf  Note the wording of bullet point 6 under the section Electrical on page 2 which states local isolation must be provided. Whereas bullet point 7. says a 30ma RCD is only recommended.  The small drawing clearly shows a local isolation point separate from the CU.

Doc H.

 
http://www.voltimum.co.uk/content/shower-isolation

if shower was in a room next to cupboard with CU in the you may be right Lurch. However I wouldn't be happy with Neutral still connected whilst I changed a shower, Neuatral being considered a 'live' conductor or Line as they like to call it these days, hence on the cert I am currently vey bored writing, we have a box for line/line insulation test result.

I also once condemmed a shower isolator for being half way down the stairs, reachable by ladder - about as much use as a chocolate teapot

 
Last edited by a moderator:
Safe isolation does not require all line conductors to be isolated. Only that no voltage is present across all line conductors and earth. 

 
it shouldn't happen but neutral, in a special location, with copper pipes - possible belt? Assuming shower isn't on RCD.

 
Last edited by a moderator:
Perhaps we should be like the yanks and refer to "hot" conductors.

Now, would neutrral be considered "hot"?

So if we are all afraid of neutral, becaise it's a "live" conductor, do you all turn off the WHOLE house just to change a broken socket front, because isolating the live to the socket circuit is not good enough as the "live" neutral is still conencted.

 
neutral is a 'live' conductor because it carries power in normal use...

but the fact that shorting neutral to earth usually trips an RCD is a pretty good indicator that there is a voltage difference (very small) between it and earth, even when line is switched off...

personally, i generally isolate at the MCB & if its dead, carry on. if the neutral and earth touch and trip RCD, then leave it til im done. not that im paranoid, but after pulling the wires apart, i usually check again, more so on the neutral on lighting circuits...

 
I f just changing a socket, I normally put the neutrals in first. Any way we digress from the post. Just trying to think if building regs require an isolator for the shower, but I haven't got my books with me.

 
Last edited by a moderator: