This really sounds like a wind up although I'm not sure you could make this up
I would agree, but its on other forms too .........
This really sounds like a wind up although I'm not sure you could make this up
Why should it be a wind up is a legitimate question? To clarify is a definite 3 phase supply each phase having its own CU , picture attached. And no there is no main switch to isolate all 3 phases at the same time, might be a good idea to install one.
So what is wrong with installing a 4 pole RCD on this board with a 4 pole isolator adjacent to the hob?
View attachment 10205
Why should it be a wind up is a legitimate question? To clarify is a definite 3 phase supply each phase having its own CU , picture attached. And no there is no main switch to isolate all 3 phases at the same time, might be a good idea to install one.
So what is wrong with installing a 4 pole RCD on this board with a 4 pole isolator adjacent to the hob?
View attachment 10205
whose bright idea was that set-up :shakehead
So what you have is a truly oit of balance 3 phase supply - can you post a picture of the metering please. If you have a 3 phase meter, that set-up is probably costing you money, not a subject I truly understand, but out of balance 3 phase metering costs you more money for the leccy than it should do. If, on the other hand you still have 3 single phase meters, then that isn't an issue, you could 3 phase the hob, not sure that is legal though???
Can somebody please explain why not, using a 4 pole RCD. All anyone say is you cannot do that please explain why. The hob is just like 3 seperate appliances. The elements are grouped into 3 banks each fed by a seperate live ie phase unless bridged out for single phase use.most TP meters dont read an imbalance, just the total of each phase
3 single meters isnt an issue either (plenty TP installs metered this way), you could fit a TP board and wire from that. what is an issue is using whats in now, wouldnt be able to take a phase from each board and combine
Can somebody please explain why not, using a 4 pole RCD. All anyone say is you cannot do that please explain why. The hob is just like 3 seperate appliances. The elements are grouped into 3 banks each fed by a seperate live ie phase unless bridged out for single phase use.
it's just a lot easier to bridge the terminals in the hob and use single phase, connected to 1 board. BY the time you've bought a 4 pole rcd, isolator, and a 3 phase board to fit it in, plus industrial isolator at the hob end , it's going to cost a lot more than using a larger cable. Something like 10mm FTE should suffice an 11 kw hob depending on the cable run, insulation in walls and any other derating factors.Can somebody please explain why not, using a 4 pole RCD. All anyone say is you cannot do that please explain why. The hob is just like 3 seperate appliances. The elements are grouped into 3 banks each fed by a seperate live ie phase unless bridged out for single phase use.
Because it's dangerous and grossly non-compliant with the Wiring Regulations as you have been repeatedly informed both here and elsewhere.Can somebody please explain why not, using a 4 pole RCD. All anyone say is you cannot do that please explain why. The hob is just like 3 seperate appliances. The elements are grouped into 3 banks each fed by a seperate live ie phase unless bridged out for single phase use.
I do not intend to take the supply from the CUs. I intend spurring a 4 pole RCBO off the henley blocks giving a seperate 3 phase supply to the hob, with a 4 pole isolator located in the vicinity of said hob.
So,today it is an RCBO
yesterday it was an RCD
just saying
so that's about £60 in parts just to avoid buying a bit of 10mm cable at roughly £3.50 /m or 17m of cable. Plus you still have to buy cable to run 2.5mm singles in conduit.I do not intend to take the supply from the CUs. I intend spurring a 4 pole RCBO off the henley blocks giving a seperate 3 phase supply to the hob, with a 4 pole isolator located in the vicinity of said hob.