Installation Method

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Lusk

Junior Member
Joined
Nov 5, 2010
Messages
111
Reaction score
0
Location
Manchester
What IM would you say for flat T&E laying on top of insulation and open to the air?  Cheers.

 
Last edited by a moderator:
102 and 103 are both described as "in a stud wall" see table 4A2 for reference, all of the 100, 102, 103, 104 refer to flat T&E buried in insulation. As this is not in insulation possibly none of these are relevant. However what is the potential of the cable being buried if further insulation is put in place?  The only Flat T&E method mentioning buried in insulation not touching any walls or joists is 103 as Essex suggested. What is the actual loading on this bit of cable in question, how critically close to its max capacity will it be running? If tolerance is not too much of an issue, pick a number or do heads or tails to decide.

Doc H.

 
Well it must be the case that securing cables to a thermally insulating material is not permitted. 

 
It is method C, there were some laboratory controlled tests carried out on cables in regards to the effects of thermal insulation which is why there are two methods referred to above. One method where the cable is fully enclosed by insulation and where one side of the cable is touching the wall for instance.

Heat will dissipate adequately enough if one surface is not enclosed by thermal insulation.

 
Surely its method  "D.I.Y"

or

method   "B.U.I.L.D.E.R"

or if none of the above got to be method "B.L.O.K.E.D.O.W.N.T.H.E.P.U.B"

:coat

who would ever leave cables lying on top of insulation anyway???

:C

 
Surely its method  "D.I.Y"

or

method   "B.U.I.L.D.E.R"

or if none of the above got to be method "B.L.O.K.E.D.O.W.N.T.H.E.P.U.B"

:coat

who would ever leave cables lying on top of insulation anyway???

:C
loft insulation installers

better than covering them up surely?

 
It is method C, there were some laboratory controlled tests carried out on cables in regards to the effects of thermal insulation which is why there are two methods referred to above. One method where the cable is fully enclosed by insulation and where one side of the cable is touching the wall for instance.

Heat will dissipate adequately enough if one surface is not enclosed by thermal insulation.


BS7671 specifically states 'not when secured to thermal insulation'. 

 
loft insulation installers


Actually most loft insulation installers I have seen the after effects of

Just bury everything under 200mm of insulation...

and most houses only just have enough slack in their loft wiring to get over the ceiling joists...

no way would they have 400mm to go up and back down again over fresh laid insulation.

:popcorn  

 
Surely no one in their right mind would be running the cables that close to their limit anyway,?

1.5 buried in 3' of insulation would still be good for 6amps driving 8lights,,,,

Ok, so maybe a shower circuit, but I think putting a 6mm on a 40amp is just cutting corners anyway, no matter how you look at it.

 