Now here is an interesting thing i just found!!!!!!
This is from the "BEAMA Guide to the Selection and
Application of Residual Current Devices"
7.2.3 Insulation tests
When insulation tests are carried out on an installation, the applied voltage should not
exceed 500V d.c. (RCDs are designed to withstand this voltage).
An RCD in circuit may affect insulation resistance test results. It may be necessary to
disconnect RCDs for the purpose of these tests.
The companies involved in the writing of this guide were apparently;
Eaton Electric Ltd
Electrium Sales Ltd
Hager Engineering Ltd
Legrand Electric Ltd
MK Electric
Moeller Electric Ltd
Schneider Electric Ltd
Siemens plc
Timeguard Ltd
Western Automation R&D Ltd
So, no worries there then!!! If you do zap one, [As i did accidently the other day!!!] just test it afterwards to make sure and carry on as normal!!
Just google "beama rcd" and click on the link. LOADS of interesting stuff in there!!!
john...
Now here is an interesting thing i just found!!!!!!
This is from the "BEAMA Guide to the Selection and
Application of Residual Current Devices"
7.2.3 Insulation tests
When insulation tests are carried out on an installation, the applied voltage should not
exceed 500V d.c. (RCDs are designed to withstand this voltage).
An RCD in circuit may affect insulation resistance test results. It may be necessary to
disconnect RCDs for the purpose of these tests.
The companies involved in the writing of this guide were apparently;
Eaton Electric Ltd
Electrium Sales Ltd
Hager Engineering Ltd
Legrand Electric Ltd
MK Electric
Moeller Electric Ltd
Schneider Electric Ltd
Siemens plc
Timeguard Ltd
Western Automation R&D Ltd
So, no worries there then!!! If you do zap one, [As i did accidently the other day!!!] just test it afterwards to make sure and carry on as normal!!
Just google "beama rcd" and click on the link. LOADS of interesting stuff in there!!!
john...
Last edited by a moderator: