Had a problem on a circuit twice in one week, 1st one movement of lighting pendant, IR tested L-N connected together to E 500v = 0.40Mohms, linked out all dimmers still 0.4Mohms eventually traced it to a transformer in one of the lights, removed it. IR now >200Mohms. I had exactly the same result while IR testing a socket circuit to add an extra socket. It turned out to be a mobile phone charger plugged in inside a wardrobe. My question is, why was getting a reading like that when L-N were connected together to earth. It seemed a bit extreme for me to remove a metalic light fitting, just to perform a minor works. Am i missing something here? What would you guys have done if you got a reading like that.
Cheers
When doing any minor works even like for like changes i always check the gas & water are bonded first, R1+R2 to the point where i am extending or fitting a new accessory, then IR test the circuit, i also test the rcd before works commence. I do a ELIT on completion. The electrician i trained with, never ever checked the gas & water was bonded or any dead tests. he just done an ELIT and tested the rcd. I always like to do things properly, after a while i find it just becomes habit.
Cheers
When doing any minor works even like for like changes i always check the gas & water are bonded first, R1+R2 to the point where i am extending or fitting a new accessory, then IR test the circuit, i also test the rcd before works commence. I do a ELIT on completion. The electrician i trained with, never ever checked the gas & water was bonded or any dead tests. he just done an ELIT and tested the rcd. I always like to do things properly, after a while i find it just becomes habit.