Isolator for shed.

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

MalcyB

Senior Member
Joined
Oct 3, 2008
Messages
317
Reaction score
0
Hi all

I'm running a 4mm SWA supply to a shed approx 50Mts away. I am going to split the tails with a Henley. Then shed will be TT and have a two way board with RCD.

Due to the position of the main board etc, it is going to be easier to connect inside the meter box. So I'm looking for a fused isolator that will fit into a small area. could anyone suggest anything?

Thanks

Malc

 
Looks about the kind of thing, but with the SWA being 4mm and the method of installation the fuse would need to be 32amp max.

 
The two way metal enclosure looks about the best option. Thanks Apache

The earthing at origin is TNCS. The board in the house is 17th Ed. The board in the shed will be TT'd and have an RCD

 
Is the bit where the SWA is connected to the plate open? I can see the Brown & Blue.

 