Got the job to install a secondary CU to feed two new circuits.
Job consisted of fitting a fused isolator into recesss elec board box, a 3m run of armed up the outside wall from the cutout box, then in to the new CU.
The naughty bit is where I had to move the E7 meter,the telemeter and a henley in the box to make room for the isolator..... "What do you mean there should be 7 tags on all the elec boards gear? I never saw any tags your honour"
Fitting the new isolator into the box took me about 2 hours!
Decided to fit a 60A isolator and run 16mm to new CU - It was a snug fit. Tried a few places to get 2 core 16mm, but could only get 3 core. Great fun using it in a domestic house!! Give me industrial/commercial any day!
The crying part, is when I had spent 3 hours installing the swa from the new CU, down the wall, into the elec box. I measured, marked and cut the armour back to terminate it into the new metal isolator...guess what I cut it about 45mm too short!!
The armour no longer reaches the metal clad isolator!!!! *cries*
Luckily I was able to stand off the gland from the isolator using a 25mm conduit coupler - there was no way I was gonna replace the cable! Pray
Anyway, I took a new 16mm earth from the head, into the metal isolator. Install new 10mm from the water and gas into the isolator too.
The cutout had 16mm tails from it into the E7 meter, then 25mm onwards. The cutout had a 100A fuse - dont you just love the elec board standards!
Oracle
Got the job to install a secondary CU to feed two new circuits.
Job consisted of fitting a fused isolator into recesss elec board box, a 3m run of armed up the outside wall from the cutout box, then in to the new CU.
The naughty bit is where I had to move the E7 meter,the telemeter and a henley in the box to make room for the isolator..... "What do you mean there should be 7 tags on all the elec boards gear? I never saw any tags your honour"
Fitting the new isolator into the box took me about 2 hours!
Decided to fit a 60A isolator and run 16mm to new CU - It was a snug fit. Tried a few places to get 2 core 16mm, but could only get 3 core. Great fun using it in a domestic house!! Give me industrial/commercial any day!
The crying part, is when I had spent 3 hours installing the swa from the new CU, down the wall, into the elec box. I measured, marked and cut the armour back to terminate it into the new metal isolator...guess what I cut it about 45mm too short!!
The armour no longer reaches the metal clad isolator!!!! *cries*
Luckily I was able to stand off the gland from the isolator using a 25mm conduit coupler - there was no way I was gonna replace the cable! Pray
Anyway, I took a new 16mm earth from the head, into the metal isolator. Install new 10mm from the water and gas into the isolator too.
The cutout had 16mm tails from it into the E7 meter, then 25mm onwards. The cutout had a 100A fuse - dont you just love the elec board standards!