I just thought I'd chuck this into the pot for a bit of general discussion....
Job last week...
customer rang to say the gas man servicing the boiler reported a very high earth reading...!
Could I come and check it out please???
So I visit the next day, Heres what I found...
1/ Gas mans report says High resistance earth (greater than 200ohms)
2/ Supply overhead TT. Whole installation protected by front end 30ma RCD.
CU is in cupboard in kitchen.
(RCD all tested working OK)
3/ A.N. Other electrician has done some minor kitchen alterations in 2009..
Cable runs from CU to kitchen will be negligible <10m.
Zs on his(/her) minor works certs is 442ohms..
No other comments or observations on cert
4/ 2 x nice newish bonding wires to Gas & Water probably installed during 2009 kitchen work.
5/ I De-energise whole installation, Disconnect 2x bonding wires off..
Do Zdb at incoming tails & CU earth bar..
get 390ohms earth loop impedance at CU.
6/ Continuity test between each bonding wire open circuit and electrical earth is <5ohms.
7/ Absolutely NO visible signs of any earth rod anywhere..
No earth wires labeled up to indicate which is the main earth..
a couple of 6mm earth wires are terminated in CU..
but no idea where they go or what they do....
8/ The property is "old" customer thinks 100ish years...
(so maybe original earth was via water pipe?????)
So........
Points for open thoughts and opinions....
a) TT with working 30ma RCD Max permissible Ra 1667ohms...
Should the gas man be concerned with greater than 200ohms...?????
b) With no easily identifiable means of earthing (hidden rod or maybe water pipe)..
Should the 2009 electrician have verified this prior to doing his work???
Reg 131.8 red book Bs7671:2008..!!
c) 2009 test reading was <27% of max permissible..
2013 reading <24% of max permissible..
4 year period no more than 3% variation of max permissable value..
stable or unstable earth re greater than 200 ohms?????
d) Have either the Gas Man or the 2009 Electrician being negligent / over zealous in their duty of care and competent work ??
Discuss???????????????
Guinness
Job last week...
customer rang to say the gas man servicing the boiler reported a very high earth reading...!
Could I come and check it out please???
So I visit the next day, Heres what I found...
1/ Gas mans report says High resistance earth (greater than 200ohms)
2/ Supply overhead TT. Whole installation protected by front end 30ma RCD.
CU is in cupboard in kitchen.
(RCD all tested working OK)
3/ A.N. Other electrician has done some minor kitchen alterations in 2009..
Cable runs from CU to kitchen will be negligible <10m.
Zs on his(/her) minor works certs is 442ohms..
No other comments or observations on cert
4/ 2 x nice newish bonding wires to Gas & Water probably installed during 2009 kitchen work.
5/ I De-energise whole installation, Disconnect 2x bonding wires off..
Do Zdb at incoming tails & CU earth bar..
get 390ohms earth loop impedance at CU.
6/ Continuity test between each bonding wire open circuit and electrical earth is <5ohms.
7/ Absolutely NO visible signs of any earth rod anywhere..
No earth wires labeled up to indicate which is the main earth..
a couple of 6mm earth wires are terminated in CU..
but no idea where they go or what they do....
8/ The property is "old" customer thinks 100ish years...
(so maybe original earth was via water pipe?????)
So........
Points for open thoughts and opinions....
a) TT with working 30ma RCD Max permissible Ra 1667ohms...
Should the gas man be concerned with greater than 200ohms...?????
b) With no easily identifiable means of earthing (hidden rod or maybe water pipe)..
Should the 2009 electrician have verified this prior to doing his work???
Reg 131.8 red book Bs7671:2008..!!
c) 2009 test reading was <27% of max permissible..
2013 reading <24% of max permissible..
4 year period no more than 3% variation of max permissable value..
stable or unstable earth re greater than 200 ohms?????
d) Have either the Gas Man or the 2009 Electrician being negligent / over zealous in their duty of care and competent work ??
Discuss???????????????