1. The meter is straight after the fuse, so should only be reading the electricity you actually use.
Do you suspect the meter is incorrectly reading your usage ?
2. From 20 Dec when the meter was installed, to 28th Feb, you have used 4651kWh.
That's 78kWh per day.
Over a year that would be 38,000kWh.
If you don't use any in the summer let's half that to 19,000kWh.
They say 17,000kWh - close ?
3. The CT is positioned to measure your total grid draw through the Consumer unit.
That's any grid used to charge the battery, all the heat pump draw, and any remaining house load.
The CT cable goes to the inverter ?
3. Whenever someone says one measurement is half the other I suspect the CT needs to be reversed.
4. I'd be embarrassed to show images of an installation that messy on this forum........ :-<