New Venture!
Well-known member
Hi all. Could I ask for clarity on something I'm puzzling over? (Currently at home suffering badly from hay fever so not thinking fully clearly!) I was asked to raise some sockets in a kitchen for a customer who wants granite splashbacks fitted. Long story cut short the electrics were installed by kitchen fitters a few years ago and are a disaster. Sockets that supplied most of the appliances were fed by radial run in 1.5mm T&E which is spurred off a 32amp ring. Customer after some discussion (and because the consumer unit is on the wall behind the kitchen) has agreed to me running a new 32amp ring to replace this and as all appliances are on one wall all good. Now the issue. On another wall there is a fused flex outlet (1 amp fuse feeding LED lighting) and a USB double socket. These are fed by 2.5mm T&E spurred from a socket in the lounge and makes a "spur from a spur" which is a no-no. Customer does not want any mess on either this wall or the lounge, nor do they want to loose either the LED lights or the socket. My idea? Derate the ring circuit from which this spur is taken to 20 amp. Customer does not have anything of any great current draw (no heaters etc) so I don't anticipate an increase in nuisance tripping. Is this an acceptable solution that means no mess or am I being stupid?