Lamp Holder Voltage When Switched Off....

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

matt.leung

Well-known member
Joined
Feb 26, 2009
Messages
1,062
Reaction score
0
Location
Bromley, Kent
Hi,

Went to a job today and found that there was 78 volts following through the lamp holder when the lights where switched off at the wall..... other than a poorly wired hidden junction box somewhere, is there another explaination for this... and i am assuming this is why bulbs keep on blowing rapidly...

 
Lamps are blowing because they are cheap crap manufactured by peasants who are paid peanuts in a factory with no quality control...

The "Voltage" is NOT there!! 

If there was 78v when off all the lamps would be glowing when off..

It is an apparent induced voltage on a conductor that is connected to nothing running in cables parallel with cables that are carrying a voltage....

(Think what you have..

one wire is open circuit at switch and open circuit at lamp = a bit of long wire acting like and aerial)

Do a search this topic has been discussed numerous times...

The fault is due to the person reading the voltage not understanding how the test meter they are using actually works..

or the concept that magnetic fields around conductors can induce current into parallel conductors...

(same principle how transformers work)

:coat

 
Canoeboy said:
You just can't beat a 

attachicon.gif
Screen Shot 2014-04-02 at 18.40.02.png
and where do you insert that then????

 
Top