Hi all, new to this forum thing but thought I best join up as I am starting to do bigger work and need confirmation at times I am doing thing OK without being OTT.
I have some lights to wire up on a sports field, it measures 90 x 60 M and the incoming supply is some 130M from the nearest corner.
I have calculated voltage drop and was coming up with 70mm supply to the corner then going off in 25mm, but this was just for the lights.
Now the guy has said he might be building an office with electric needed. I saw the plans for this for the first time today and it's a bit bigger than I expected and has electric heating!
Re calculated and am getting 95mm supply cable (130M run) and a 70mm to office (90M run).
Calcs: 130(M) x 50(A) x 0.43(V) = 2.795 volts dropped to first dist point
90 (M) x 50 (A) x 0.57 (V) = 2.565 volts dropped to office position
Is this looking sensible as it seems mad that these are the cable sizes and he didn't like the phone call to say the cable bill alone has gone up by a lot?
Thanks for any advice.
I have some lights to wire up on a sports field, it measures 90 x 60 M and the incoming supply is some 130M from the nearest corner.
I have calculated voltage drop and was coming up with 70mm supply to the corner then going off in 25mm, but this was just for the lights.
Now the guy has said he might be building an office with electric needed. I saw the plans for this for the first time today and it's a bit bigger than I expected and has electric heating!
Re calculated and am getting 95mm supply cable (130M run) and a 70mm to office (90M run).
Calcs: 130(M) x 50(A) x 0.43(V) = 2.795 volts dropped to first dist point
90 (M) x 50 (A) x 0.57 (V) = 2.565 volts dropped to office position
Is this looking sensible as it seems mad that these are the cable sizes and he didn't like the phone call to say the cable bill alone has gone up by a lot?
Thanks for any advice.