Well,if it was me I would be testing at the source first
test lighting run second
measure "assumed" length of cable
do,a,couple of sums and see if the theoretical answer was same as measured one
dont just think ."oh that's it so it must be ok"
just saying
A 200m drive leading to a house has lighting bollards every 10m . The zs from the last bollard is 28 ohms this is to high for the protective device, can i just fit 30ma rcd protection and will this satisfy the ECR