Is this breaker an MCB or RCD?
If you only have one lighting circuit, this suggests to me that the wiring could be quite old?
As for many years it has been good practice to split lights and sockets across multiple circuits during rewires / Consumer unit replacements so that in the event of a fault you do not lose all lights or all power..
If the wiring is quite old, (I am guessing your breaker that tripped may be an early MCB and not and RCD or RCBO?..) then the various cable joints will also be old...
And old joints and cable terminations where conductors have been squashed into screw terminals that have been subject to the heating & cooling effects of electricity passing through them for years can finally break down during an increased current flow during a lamp failure..
I have known a halogen lamp to blow and also burn out a cable joint part way down the lighting circuit...
However lights are wired as radial circuits, and can have branches anywhere... e.g. at junction boxes, switches, light fittings...
So you cannot assume the order anything is wired in, unless you have tested and proved the circuit with suitable test gear..
The only assumptions you should ever make during any fault investigation is that: "Everything is faulty, until you have proved otherwise"
If you don't have access to any suitable test kit then it is going to be quite difficult to prove you have fixed the problem..?
As sometimes visual inspection of a joint does not immediately show a failed continuity between conductors.
I would have started with some dead continuity and insulation resistance tests, (L-N, L-E, N-E)..
Disconnecting the circuit from the consumer unit, and using my various plug-in lamp adaptors to minimise the amount of accessories I need to open up...
Then depending upon the results I get I would probably find somewhere to split the circuit at a mid-pint to do further tests..
e.g. a good test meter and a set of adaptors similar to these can save hours of faffing around opening up accessories and possibly putting more faults onto the wiring?
https://www.test-meter.co.uk/megger-la-kit-lamp-adaptor-testing-kit