Hello everybody I need your advice in a twisted matter that I found today when opening a consumer unit I noticed that live was connected to a yellow/green 16 cable directly to the main earth connection of the TN-S system....I will disconnect everything tomorrow but why the British Gas engineer did that (I was told) ....beats me...????

 
I doubt it is a live cable if it is connected to earth. Probably just a dead red or brown insulated wire that is now earthed. Or are you actually saying there is no earth on the installation and all exposed and bonded metal parts are now at supply voltage with respect to earth?

Doc H

 
As all the others have said, i doubt its a live cable but a red/brown that has been used as an earth or a disused cable shorted to earth as it should. Dont remove whilst the instalation is live untill you have proven where it goes and what it does

 
 You say  " A yellow/green 16 cable  connected to the main earth terminal "

So that must be the actual main earth  ( 16mm2 )    to clarify things .......  it enters the consumer unit  and is conected to a  "Live "  cable . do you mean a red or brown cable  ?  Is it to extend the 16mm G/Yell ?    Does it go to the earth bar ?      Does it merely need some Green/Yellow tape on it ?   Is this "Live " cable 16mm ?

What has the Gas man got to do with it ?

 
Last edited by a moderator:
Have a look at your copy of the memorandum of guidance to the electricity work regulations, which you should be fully acquainted with as it explains your statutory obligations under the EAWR 1989.  

Here's the relevant bit to save you digging out your copy, with my underlining for emphasis.

Disused electrical equipment and systems
75 Before electrical equipment is decommissioned or abandoned for any reason it should be disconnected from all sources of supply and isolated. Isolation (as defined in regulation 12(2)) requires taking effective steps to ensure that it is dead and cannot become inadvertently re-energised or charged by induction or capacitance effects. (Regulations 12, 13 and 14 are also likely to be relevant.) Suitable labels or notices to bring people’s attention to the state of the equipment are likely to be necessary in preventing inadvertent re-energisation.
 
One way of complying is to connect all the unused lives to the main earth, which may be what you have, as others have pointed out.
 