Sharpend
"It Just Is"
Generally any roof supporting structures can not be drilled.
Really?Generally any roof supporting structures can not be drilled.
After a freshly submitted TMA I had the same discussion The BCO was dumbfounded when I presented my evidence.I had this very discussion with a BCO a few months ago, & he said exactly what you said.
Then I stated that it was OK to drill if it was done on the neutral axis.
At this point he was speechless.
He then went on to quiz me about neutral axes and beam loadings etc.
Once I had explained and answered his every question (even though I was not involved in "drilling" structural beams), then he relented and said, that, yes, if I did it my way then it was fine.
They do not allow it, because it is not done correctly, thus they find it easier to not allow it, rather than have to explain or get remedial works done.
Have you never seen a castellated beam?
Fixed that for youyes, in metal beam only, knot roof timbers.
There might be a couple that could be re-routed, but most run a pretty direct route from one point to another straight over the top of joists with not much slack. I only want to put a few boards down, I didn't really want to get into replacing cables!!!
The thing is,There can't be that many cables if its just an average domestic property.....
2 or 3 bedrooms..
Landing...
bathroom...
If your only putting a few boards down then I guess not every cable will need moving....?
Surely the cheapest solution is just get the few cables re-routed and save prating around with batten and spacers etc...
and have no risk of squashing a cable as they will all be out of the way.
opcorn
The thing is,
Insulation depth.
I live in a 2&1/2 bed semi, have you seen that mess of cables on my gable wall,? :C
Not much of an issue for lighting.....
1.0mm worst case de-rated down to 8A enclosed in insulation in a stud wall....
or 1.5mm down to 10A enclosed in insulation in a stud wall...
{method 103}
or if we go above a plasterboard ceiling under greater then 100mm insulation {method 101}
we still have 10.5A or 13A to play with for 1.0mm & 1.5mm respectively.
Assuming were on 6A circuits here... Just re route and cover the lighting cables...
still can't see much of an issue....
From what the OP said I don't read this a shower cables....
Which would be a different ball game altogether.