Hi I'm looking for some advice well ideas really.

I have a customer who owns. A shop with large amount of displays, he's looking to have these digital photo frames in the middle of each display for work he's carried out.

So basically he has 35 displays so wants 35 sockets installed for these photo frames. Then he wants to be able to turn so many sockets on via a switch to save turning each socket on individually.

I'm exploring ideas but wondered if you guys have any advice as not something I have tried before so I'm open to suggestions.

Any links etc would helpful.

Thanks in advance

 
Since they will all be low power, put them all on one radial circuit, switched from an FCU with a 13A fuse in it.

you can then put them on a timer as well (immersion heater timer?) if you want them automatically on and off at certain times of day.

 
No need for 13A FCU...

all the plugs will have their own local fusing...

Just do a 16A or 20A radial with as many sockets as you want....

A 20A DP switch at a suitable location to switch them all on/off..

Guinness

 
Hi I'm looking for some advice well ideas really.

I have a customer who owns. A shop with large amount of displays, he's looking to have these digital photo frames in the middle of each display for work he's carried out.

So basically he has 35 displays so wants 35 sockets installed for these photo frames. Then he wants to be able to turn so many sockets on via a switch to save turning each socket on individually.

I'm exploring ideas but wondered if you guys have any advice as not something I have tried before so I'm open to suggestions.

Any links etc would helpful.

Thanks in advance
I would do what the others have said, running a radial to back box.

but if want to turn certain areas on and off could then have bank of 4/8/12 DP isolators, and run them to 4/8/12 socket circuits. Timers could be added.

OR

to a wisebox and have different banks controlled by remote.

 