For Monkey5 and Badger, I see you didn't get a reply to your question so here's the amswer.You divide the 230 volts by the 3.65 megohms and it gives you the value 0.000063 amps. This of course is only when nothing is plugged in and switched on. My advice would have been, do the test with nothing connected to the ring, after all, you are supposed to be testing the 'hard wiring only', not any appliances as well, that's what Portable appliance testing is for. The method you used is really to save you time disconnecting things like dimmers, indicator lamps, transformers etc. So assuming a client is paying you to do the testing, you should suggest that P.A.T. testing is a separate job/contract from installation testing and you then negotiate a separate price for each job.
3. Was it unreasonable to ensure all items were disconnected because I think really the guidance is to do L/N to E where it would not really be practicable to do the normal tests ie lighting ccts with loads of trannies.
In a perfect world yes... Disconnect everything,
take all the time in the world,
the customer doesn't mind they will pay the extra 3 hours hide & seek disconnecting & reconnecting everything
just to verify what you already know is safe and compliant with regs is Actually still safe and complaint with regs!
:|
You are both missing the point that OFTEN is is very impractical to FULLY disconnect everything from a ring main as well, not just lights ...
consider...
1/ An security alarm panel connected via a NON switched fused spur (to prevent anyone accidentally turning it off) taking ye ole fuse out don't disconnect the neutral from the appliance!
2/ That 4way multiblock with integral neon that has been plugged into the socket which is now behind the wardrobe / Bunk-bed / Chest of draws that don't move easily or NOT at all.
3/ That 6way multiblock with integral surge filters with all the computer stuff plugged in, that has been plugged into the socket which is now behind back of the draws on the computer desk wot you cannot get enough room to get the plug out!
4/ The multiple group of sockets right at the back of the TV & video or hi-fi equipment that is now built into the back of a cabinet or is not physically possible to reach without dismantling entertainment system or moving the large TV unit.. that needs two or three people so that the legs don't break off the unit!
5/ That socket in the kitchen with the extractor hood plugged into it, wot the builders hid behind the decorative chimney bit... but you need to take the extractor hood down to get to!!!
6/ And that socket underneath the kitchen units wot the plinth heater has been plugged into..... And you need to dismantle the plinth to get to it!
7/ The socket that the built in dishwasher is plugged into, that the git kitchen fitters didn't an isolation switch for, and you cant dismantle and remove the dishwasher.
8/ The socket behind the big American fridge freezer that cant be moved unless it is emptied!
9/ The socket everyone forget to tell you about and you cant find hid down the corner of a bedroom with a room fragrance thingy still connected.
10/ That doorbell transformer that may have been wired onto the ring via a non switched fused spur (cuz they didn't want to accidentally turn the doorbell off!)
11/ The bit of power in the conservatory that had been extended off the ring, supplying sockets and the lights also put off a Non Switched fused spur so no-one accidentally kills the supply for the light!
12/ The outside security PIR sensor light that DIY bob connected to a non switched fused spur in the bedroom.
13/ An RCD fused spur hard wired in supplying the garden pond pump? reading across the back of the RCD?
14/ An RCD socket outlet reading across the back of the RCD? open up & disconnect?
etc...
etc...
:_|
There are many instances where you find something connected electrically safe... but a sod to disconnect for testing!
Ideally it is nice if you can disconnect everything....
But quite often it is simply just NOT practical, even on socket circuits not just light!
OR
you could just read the Notes on Reg 612.3.2
AND ESPECIALLY
reg 612.3.3 page 158 BRB
wot says quite clearly test between the LIVE conductors together to Earthting arrangement.
Guinness