Did some pre-upgrade checks on a customer's wiring today to see if they're ok for a new consumer unit.
The cooker and the immersion heater circuits had L-E and N-E IRs of about 0.17M ohms. The pump and heater element where still connected. The cooker when disconnected did not improve the result of the cooker circuit, so i'm guessing poor wiring.
The cable looked silver, I think tinned copper - so must be pretty old?
The other circuits have IRs above 3M ohms. I think they are probably due a rewire.
My question is, what is the lowest IR I can get away with without tripping an RCD?
By my reckoning, the lowest total resistance of live and neutral to earth can be 7k ohms or above before it will trip an RCD. Which I get by doing 230/0.03. 0.03 being 30 milliamps.
I don't have an earth leakage clamp meter unfortunately. I intend to make the cooker and immersion heater non RCD circuits, and the others on the RCD.