Remember, when you do this you should leave the earth connected to make sure that a cable isn't shorting out through pipework or similar.... got picked up on this during an assesment onceSorry and one question I forgot to answer.. yes I disconnected all conductors to keep them separate when testing. Originally I did a global IR and found it low so went on to do circuit by circuit.
Wylex Fully Insulated RCD Shower Consumer Unit - Screwfix.com, Where the Trade BuysThat was an option I gave them, but they were already thinking about a new CCU. I believe you can get standalone RCD enclosures for adding protection to an existing circuit.
If cooker hood and pump are still connected to circuit, then it is still posiible that these items are causing low readings - I would suggest retesting but between L&N together to earth with circuits disconnected at CU. This helps protect appliances from 500V, and is an acceptable means of testing where items are hardwired to circuits. As for 3Meg, the official position as I understand it is that any circuit that passes test is good for ten years (domestic property). Personnally I would not be happy with these numbers, and would suggest re-testing at a lower timer interval, but if customer cannot afford re-wire at the moment then this is one way to proceed. Changing CU would improve protection of cables, and protect customers better. If you decide to continue with this I would however state on certificate that in your professional opinion that the property would benefit from additional works (ie re-wire or intensive test/fault finding) given the low IR readings obtained.The cooker circuit I am sure is the cabling, no loads were connected when I did the last IR test. The immersion circuit L-E was tested with the FCU switch to the immersion off, so the test would not have included the element. The water pump was connected still though.