Just a note on this; Gn 3 states that testing is to be
carried out where practicable. Reg 612.2.1.
If the calculation for conductor size is carried out correctly,
and a size is between any two sizes in that table, then,
obviously, the next size up is used.
Re Ultinator's point, supplementary bonding is not always
required. See Reg. 701.415.2.