When compiling a EICR or Installation cert what do you fill in for the main earth size when usually a 16mm cable has been taken to the MET but (again usually) the suppliers short cable is 2.5-4 mm ? This would normally only arise with a TNS supply
So only 2 people are prepared to say what size cable they note on a certificate, the cable on the consumers side of the MET or the suppliers side ?
Although it doesn’t fall in the remit of BS7671. If you’re unhappy with the supplied earth connection you could use a constant pressure spring and braid, not a BS951 clamp.