6mm earthing conductor from board to rod. Next to rod is gas meter position - 10mm bond from rod to gas pipe.Bonding should be back to MET. MET is not MET if Earth is not in it. Given that its also different sizes we can assume its not continuous either so removing the gas bond will loose the Eath all together.Code 2?
What if the rod is the METBonding should be back to MET. MET is not MET if Earth is not in it. Given that its also different sizes we can assume its not continuous either so removing the gas bond will loose the Eath all together.Code 2?
How can it be? Is the CU directly connected to it? If anything the Gas pipe is the MET but the cable sizes still should be the same.What if the rod is the MET
16mm tails would allow a 10mm to the rod from MET, but require a 16mm from MET to CU,I read that round the other way (as in MET-pipe-rod). Rereading it then thats just lazy. Still agree its a code 2 and there should be a 10mm to the pipe and 16mm to the rod (assuming the supply cables are >15mm).