Oh ! Who mentioned adjustable breaker / Is he turning it down to 60A ? Thats a dfferent kettle of hamsters.
The "NEW" GN8! ; )I wish i knew what i was doing half the time, I have lost my glasses now and cant find the bottle opener.....GN8 has the Armour Equivalent tables in it
Your Boss is NOT competent to be doing this work. End of. Tell him so, for the sake of the client.however when I brought this up with the boss, he said that it's not a problem as the 16mm feeds either a 100amp board or 63 amp board with a FUSED isolator fitted adjacent to each sub board. Therefore he says that as each 16mm feeds a board which is equally balanced across phases (ie 33 amps at the max per phase) a 16mm conductor is capable of taking the load. What I have tried to explain is if there is a fault on one of the circuits the 16mm conductor may take 100amps before the FUSED isolator pops (or more which is usually the case with fuses) therefore melting the cable.