I have recently had four storage heaters fitted by an electrician.
This is a completely new installation, including consumer unit and MCBs
There is one 3.3 kW storage heater, two 2.6 kW and one 1.7 kW
The four MCBs for the storage heaters are each rated at 20 amps
Is that correct for the above storage heaters?
I would have expected one 10 amp and three 16 amp MCBs
What is an expert's view on this please?