I have a question about sizing the MCCB and the cable for a 55kW 3 phase motor.

I have done following calculations and please correct me if wrong. 

FLC = 55000/(1.732*415*0.8) , (I have assumed the PF as 0.8),

FLC = 96A 

Main,delta Contactor & Over load realy;

96*0.58 = 56A,

Star contactor;

96*0.33 = 32A

If above calculations are correct what would be the ratings of MCCB/MCB 

MCCB little over 56A  would be enough for the starter?

or

Do I need to consider about the high transient current.

And when selecting a cable, would cable which can handle 10A be enough for the starter or again Do I need to consider about the high transient current.  

 
 