I have a question about sizing the MCCB/MCB and the cable for a 9.3kW 3 phase motor.
I have done following calculations and please correct me if wrong.
FLC = 9300/(1.732*415*0.8) , (I have assumed the PF as 0.8),
FLC = 16.17A ( 17A)
Main,delta Contactor & Over load realy;
17*0.58 = 9.86A (10A),
Star contactor;
17*0.33 = 5.61A ( 6A)
If above calculations are correct what would be the ratings of MCCB/MCB
MCB little over 10A (type C) would be enough for the starter?
or
Do I need to consider about the high transient current.
And when selecting a cable, would cable which can handle 10A be enough for the starter or again Do I need to consider about the high transient current.
I have done following calculations and please correct me if wrong.
FLC = 9300/(1.732*415*0.8) , (I have assumed the PF as 0.8),
FLC = 16.17A ( 17A)
Main,delta Contactor & Over load realy;
17*0.58 = 9.86A (10A),
Star contactor;
17*0.33 = 5.61A ( 6A)
If above calculations are correct what would be the ratings of MCCB/MCB
MCB little over 10A (type C) would be enough for the starter?
or
Do I need to consider about the high transient current.
And when selecting a cable, would cable which can handle 10A be enough for the starter or again Do I need to consider about the high transient current.