Megga MST 1552 Help

Help Support Talk Electrician Forum:

beemer

Member
Joined
Mar 27, 2008
Messages
56
Reaction score
0
I have a colleague who has recently passed his C&G2391 (we were on the same 2330 course for 3 years) and has a job with an electrical company in the testing section. He has been given a Megga MFT 1552 tester and seems to be having problems with his Pfc readings.

The situation is he gets a pfc of around 4KA at origin but his companies parameters are 1.9KA max. He thinks he might be doing the test wrong.

His instructions indicate that he needs only use two leads when testing L-N for psc and L-E for pfc.

Is this correct? I don't know the Megga (I have a Meterel) so can not help him.

Thanks in advance..

Dave

 

steptoe

of course Im wrong, ask my wife™
Joined
Feb 13, 2008
Messages
24,344
Reaction score
119
Location
Gtr Manchester
its exactly the same test,

just on different cable.

dunno what 2 leads a megger uses, but lets say its the Ph + E, then you do the test across phase + earth, then put your earth lead on the neutral cable and repeat the test, use the highest reading.

remember on 3phase to use the correction factor,

PFC and PSCC IMHO are the same thing,.

or tell him if he gives me

 

norv

Senior Member
Joined
Feb 16, 2008
Messages
127
Reaction score
0
I always use the 2 leads on my 1552 & put the setting on PFC HI.

 
Joined
Mar 7, 2008
Messages
9,994
Reaction score
0
Location
In the office again.
I have a colleague who has recently passed his C&G2391 (we were on the same 2330 course for 3 years) and has a job with an electrical company in the testing section. He has been given a Megga MFT 1552 tester and seems to be having problems with his Pfc readings.The situation is he gets a pfc of around 4KA at origin but

his companies parameters are 1.9KA max.

He thinks he might be doing the test wrong

His instructions indicate that he needs only use two leads when testing L-N for psc and L-E for pfc.

[/uNQUOTE]

Is this correct? I don't know the Megga (I have a Meterel) so can not help him.

Thanks in advance..

Dave
A Ze of 0.12 at Uo 230v will provide approx 1.9KA. 0.05 will give 4KA. On TN systems (esp. PME), readings as low as 0.01 are not uncommon (i.e. 10KA+)

The third lead allows for non-tripping RCDs on Zi testing (though apparently the new meggers can do this with 2 leads??)

HTH

 
Joined
Mar 28, 2008
Messages
13,621
Reaction score
297
so whats the difference?on any system,

between the fault current and the short circuit current(which is simply a FAULT)

its always the highest reading that is used

?:| ? :|
To my understanding..

PFC: is the fault current between phase & earth.

live - earth fault!

PSCC: is the fault current between phase & neutral

live - neutral fault!

They can be different!

and as you say Highest value is used! :D

 

steptoe

of course Im wrong, ask my wife™
Joined
Feb 13, 2008
Messages
24,344
Reaction score
119
Location
Gtr Manchester
the actual readings may be different,

but as I understand it that is why it was changed from simply PSCC to a PFC reading.

a FAULT is a FAULT, doesnt matter if its a between phase neutral, or between phase earth.

its all about the prospective highest current that will flow in the circumstances.

 
Joined
Mar 28, 2008
Messages
13,621
Reaction score
297
the actual readings may be different,but as I understand it that is why it was changed from simply PSCC to a PFC reading.

a FAULT is a FAULT, doesnt matter if its a between phase neutral, or between phase earth.

its all about the prospective highest current that will flow in the circumstances.
Yes M8.

I think the point being if using some three lead testers..

you need to stick your leads across red (L)- black(N)- Green(E)

or brown/blue etc.. to read live earth fault.

then stick green onto (N) to read live neutral fault.

then stick down the biggest value on your cert. :)

 