Megger mft1553
Am i right in what im saying here
Ze
open main switch to db.
Remove main earth
Use red+green leads
high loop setting
Measure between cpc+line
Record results in ohms
PFC
Reconnect main cpc
Use red+green black leads
Test between cpc neutral line
Pfc setting
Record results in KA
Zs
Testing live circuits with rcd protection
Use red+green+black leads
Measure between cpc+neutral+line at end of circuit
No trip setting
Record results in ohms
Am i right in what im saying here
Ze
open main switch to db.
Remove main earth
Use red+green leads
high loop setting
Measure between cpc+line
Record results in ohms
PFC
Reconnect main cpc
Use red+green black leads
Test between cpc neutral line
Pfc setting
Record results in KA
Zs
Testing live circuits with rcd protection
Use red+green+black leads
Measure between cpc+neutral+line at end of circuit
No trip setting
Record results in ohms