Hi - looking to pick brains and confirm my own thoughts. Iwas called to a house today as the shower had stopped working. Checked the wall mounted 45A switch and both line & neutral terminals on load side had melted. The circuit checked out fine- low zs, clear on insulation test. The shower is a 8.5kw on a B32 mcb & rcd protected-neither breaker orrcd have tripped. Would the likely cause be loose connections when originally installed? Appreciate some guidance if my thoughts are incorrect.