Just wondered if anyone has used theese MK kits with 10 breakers fitted supplied.
Lid slightly different and cheaper RCDS fitted to unit.
Had a situation today while doing a CU change when testing the ze at this unit to be 0.10 ohms as it is close to transformer TNCS i teasted a radial circuit 2m long wired in 2.5mm cable supplying one socket outlet i found the loop impedence to be 0.60 ohms.
this was with a megger MFT1552 tester on trip lock, i tested the RCD on the incoming side and found 0.10 ohms and on the load side o.38 ohms.
Has anyone found the extra resistance theese units add to the circuit.
I had this problem a few years ago with some old Hager BS4293 RCCB.S that did the same to the ircuit to such a large factor