I and other collegues routinely inspect hot burger trailers and we are somtimes shown documentation( EICReports) showing that it has satisfactory earthing arrangements- how can we be certain that the certificate is valid and what should we be looking for which might indicate that there isnt adequate earthing ( we rely on visual checks only and none of us have any testing equipment)?
I apologise now if a) you all shout at me for asking a question which is covered by the On site guide b) rely on more experienced engineers to base an opinion and c) I appear gormless but I thought that this forum may provide guidance and help with an issue which sometimes worries me and which I have not yet resolved in my own mind. Thanks
The mobile units I have worked on and wired that rely on a genny for power use electrical separation as the protective measure, therefore there won't be an earthing arrangement as such. Most of the ones I have tested have relied on ES also. With regards to ES as a protective measure, some of the things you'd need to ensure (include but are not limited to) are that all class 1 accessories and the metal frame of the unit are all bonded together, the protective devices are all double pole and that the generator and supplying cable are suitable for use (no bond between the frame and a live conductor, not V-0-V configuration etc...).
As Andy above has already pointed out, an RCD is next to useless on such a system and I'd be surprised if one was installed if the trailer is only ever going to be supplied by a genny, therefore an assumption can't be made that the trailer is safe just because it has an RCD fitted. You'd also need to ensure that the installation was already under the supervision of a skilled or instructed person. As an example, one of my friends dads owns three mobile burger vans, each one of them I have rewired, and each installation I am continually responsible for as the skilled person. They each get tested, rigourously, on an annual basis, and any alterations (if any) would be made by me and me alone.
If the trailer's supply is a rodded genny or supplied from a TN system, therefore allowing for ADS as a protective measure, well, that's a whole different ball game
We then delve into the dark depths of 'how to make a good TT system' lol (regarding referencing eaths at the genny [technically not a TT system]). This is another conversation entirely. ProDave has also already covered where the trailer is supplied via PME.