W whazza2 Senior Member Joined Jun 4, 2010 Messages 183 Reaction score 0 Jul 20, 2010 #1 What should the overload be set to for a three phase 0.5kW motor?
Andy™ ©Resident Geordie™ Supporting Member Joined Jan 1, 2009 Messages 30,747 Reaction score 1,472 Location S. Tyneside Jul 20, 2010 #2 0.5kw?
W whazza2 Senior Member Joined Jun 4, 2010 Messages 183 Reaction score 0 Jul 20, 2010 #3 Yeah which is 500watts. Do you divide by 3 as its three phase, then divide that by 230?
Andy™ ©Resident Geordie™ Supporting Member Joined Jan 1, 2009 Messages 30,747 Reaction score 1,472 Location S. Tyneside Jul 20, 2010 #4 you use square root of 3 - which is 1.73
L Lee321 Distinguished Member Joined Sep 8, 2008 Messages 2,141 Reaction score 0 Jul 20, 2010 #5 have to use the 3ph pi calc thing Amp= kilowatts X 1000 ----------------- Volts X PF X 1.73
W whazza2 Senior Member Joined Jun 4, 2010 Messages 183 Reaction score 0 Jul 20, 2010 #6 Whats the answer to that
L Lee321 Distinguished Member Joined Sep 8, 2008 Messages 2,141 Reaction score 0 Jul 20, 2010 #7 about 1 amp