Whilst troubleshooting a PV system fault (maybe more of that later but it’s not the issue here) my electrician found 235v L-N 202v L-G and 30v N-G. He disconnected everything including all N and G tails, same result. Fitted a new Earth rod, same result. Called supplier who disconnected the house completely (which incidentally includes the complete PV system) and found 235v L-N and said “earth problem - we don’t supply it, your problem mate”.
I asked them to check L-G and N-G (my earth rod)whilst house was completely disconnected , they found 202 & 30 but still said your problem mate. I have checked next door who are on same supply, also TT system, they have 235/0/0.
Supplier checked his supply cable between transfo and me, don’t know how, says it’s ok. So supplier says supply ok, it’s a house problem, my electrician says house is ok, I’m going to try to get them both here together.
Anybody ever seen this before? Neither electrician nor supplier has apparently
I asked them to check L-G and N-G (my earth rod)whilst house was completely disconnected , they found 202 & 30 but still said your problem mate. I have checked next door who are on same supply, also TT system, they have 235/0/0.
Supplier checked his supply cable between transfo and me, don’t know how, says it’s ok. So supplier says supply ok, it’s a house problem, my electrician says house is ok, I’m going to try to get them both here together.
Anybody ever seen this before? Neither electrician nor supplier has apparently