Came across one that finally taught me otherwise:
https://www.youtube.com/embed/M8phlIi42qY?feature=oembed
https://www.youtube.com/embed/M8phlIi42qY?feature=oembed
Hello Martin, as you know an electrician in the UK would carry out a full test procedure on a suspect RCD or while doing post installation certification testing.
BTW, is this how you damaged your test leads (MH).
Sounds like you need a "17th edition" multi function tester!
:lol:
I was under the impression that GFCI'S were a new addition to the American regs but what would I know!
So the whole problem with earth leakage it dealt with by not having an earth! :lol:
Good Morning,
Tuesday, we received the GFCI from the YouTube video (link below) and performed an analysis of the product. The sample is identified as a Phase 7 style GFCI, with date code 1A10I (January 2010).
https://www.youtube.com/watch?v=MGQXsCc11qc
Using an Ohm meter, the GFCI was initially found to have welded Phase side face (receptacle) contacts. When the sample was opened, the weld broke. In accordance with our safety certification and in production, multiple tests are performed to assure this does not occur. On a weekly basis Endurance, Low Resistance Ground Fault, Extra Low Resistance Ground Fault, Short Circuit and Overload tests are performed. These tests evaluate the GFCI’s ability to open a circuit under extreme conditions. Therefore this weld is an extremely rare occurrence. This typically indicates the GFCI has seen significant use/abuse and/or an overcurrent condition (see image below). In this instance, we believe an overcurrent condition is the most likely cause.
The video posted on YouTube demonstrates the user connecting a light bulb from the Phase face contact to ground. With the GFCI contacts welded, the device will provide power from the Phase side even when the device is tripped, as the video shows. However, when the bulb is connected from Phase to Neutral on the face, the bulb does not light up. This is because the Neutral side was not welded and those contacts were open preventing the flow of electricity. The sound that can be heard in the video when the light bulb is connected from Phase to ground, is the GFCI firing the trip solenoid in attempt to remove the fault. Since there is welded contacts, the device will continuously fire when there is a fault until it burns the coil open. It appears that the end user continued apply a fault even after the video ended since the trip coil is burned open (large red circle in image below.)
7. The user must test their RCD every 3 months.
That's what he just said?and we all know everyone tests the RCD every 3 months...
Mbrooke,
Hopefully there are a few things here that would not be an issue in the UK.
1. We use earthed socket outlets.
2. We verify that the earth is present and adequate after installation.
3. We have to verify by design and measurement that any device is capable of interrupting the fault current at the point of installation. Therefore contact welding would not occur due to fault current overload.
4. The higher voltage we use results in lower load currents.
5. The higher voltage we use assists in the self cleaning arc for the contacts during operation, thus, the contact resistances are lower therefore less Joule heating across the contacts.
6. The EN standard requires linked contacts thus the mechanism of both contacts is self assisting.#
7. The user must test their RCD every 3 months.
Therefore this occurrence should be extremely rare in the UK
Our sockets are earthed as well, but we lack most of the other. BTW, wont high voltages result in contact pitting thus more chance of contacts welding shut?