Hi,
I have a job to connect up a Single phase sunbed in a salon. I have telephone the manufacturer for the spec of the sunbed. They have told me I must use the following; 63A type c circuit breaker, 10mm cable into 63a rotary isolator & the circuit is to be protected by a 100ma rcd. I have asked for these instruction to be e-mailed to me. They said they do not give out exact spec's as they have a problem with electricians quoting much higher starting currents. Also the 100ma rcd must be used & dont be tempted to put in a 30ma.
The DNO have installed a new meter especially for the sunbed. 100A fuse. TNCS
I intend to do the following; from suppliers isolator 25mm tails into an 80a switched fuse. Out of the switched fuse with 16mm 3 core swa for 16 meters to ccu. I will earth the armour & also use the 3rd core as an earth. I have used 63a as design current, the cable will be clipped direct which gives me 77Amps & volt drop of 2.41v. (which I got from pages 334 & 335 of the brb). I will go from the ccu with 16mm T&E straight into a rotary isolator. Then connect the bed
Does the above sound o.k, have I missed anything. (be gentle)
Cheers
I have a job to connect up a Single phase sunbed in a salon. I have telephone the manufacturer for the spec of the sunbed. They have told me I must use the following; 63A type c circuit breaker, 10mm cable into 63a rotary isolator & the circuit is to be protected by a 100ma rcd. I have asked for these instruction to be e-mailed to me. They said they do not give out exact spec's as they have a problem with electricians quoting much higher starting currents. Also the 100ma rcd must be used & dont be tempted to put in a 30ma.
The DNO have installed a new meter especially for the sunbed. 100A fuse. TNCS
I intend to do the following; from suppliers isolator 25mm tails into an 80a switched fuse. Out of the switched fuse with 16mm 3 core swa for 16 meters to ccu. I will earth the armour & also use the 3rd core as an earth. I have used 63a as design current, the cable will be clipped direct which gives me 77Amps & volt drop of 2.41v. (which I got from pages 334 & 335 of the brb). I will go from the ccu with 16mm T&E straight into a rotary isolator. Then connect the bed
Does the above sound o.k, have I missed anything. (be gentle)
Cheers