been installing a new supply to a garage today, due to somebody a friend of the owners family installing a 1.5mm 3core lighting armoure to feed a light/3 twin m/clad sokets and 2 spurs in the garage some 25metres away from the main c/u in the house, PArt p really is working isnt it :innocentheadbang

job done by owners mate!

Image658.jpg


anyway after working our the mV/A/M calcs i worked out on a 15amp total load on that 1.5mm it would have approx 13 volts drop under full spec'd load, this is above the 3% max allowed ie 6.9volts, so worked it out again using a 4mm armoured and it calcs to 5.2 volts approx, so within limits.

anyway job for today was install the 4mm armoured, with twin m/clad socket, m/clad spur and new flourescent light fitting, oh i replaced the c/u in hallway yesterday and part rewired the kitchen lights and fitted that new flourescent, plus rewired the oustide light on the front, and a couple of other things were done like alarm/toilet downsatirs light and fan rewired anf done correctly inc new isolator spur @ 3amp for the fan. extra/rewired sockets upstairs, and new socket fronts, plus conservatory has had a couple of altertions, so all in all a nice job, heres some piccies anyway.

kitchen light

Image660.jpg


c/u in hall

Image661.jpg


old c/u in place where that adaptable box is where cables were crimped/extended.

Image662.jpg


garage supply pictures:

Image663.jpg


Image664.jpg


Image665.jpg


Image667.jpg


Image666.jpg


Image668.jpg


Image669.jpg


Image670.jpg


 
Like the pics nice work, but i cant see next inspection sticker on cu but i do have a cracked laptop screen.SLAP

 
Can't see a schedule of circuits either;) ;) ; )
its on the board called the labels :^O

---------- Post Auto-Merged at 12:46 ---------- Previous post was made at 11:28 ----------

if your all wondering y there is a mcb on the unprotcted side thats cause it feeds the alarm system as i had to rewire that to get it off the lighting downstairs. :p :^O

 