Hi, Hoping someone may be able to point me in the right direction.
Over the past few months have been installing the following: Multiplus 2 48/5000, Seplos 280Ah battery, Venus OS running on Raspberry Pi with display. 230v is connected to AC In, ESS enabled with CT clamp connected to the 3.5mm plug in inverter to monitor grid.. These are installed in garage and connected to a consumer unit in garage. This is in addition to a seperate Solaredge PV system that was installed last year. I will eventually fit a current sensor to the Solar PV output to show PV but that'll be in the future.
Fired the whole thing up yesterday morning and all was working as expected. Battery charging when producing excess solar and then supplying house load when insufficient solar. Charged car from battery at 3kW to check for any cables or connections getting hot. All ok.
During the afternoon I inadvertently touched the main breaker test button in the consumer unit and everything shut down. Switched everything back on and now for some reason the display is showing a PV Inverter connected with around 7kW and the Grid is now showing -7kW. Reset everything and have went through all the settings to see if anything had changed. In the device list it is showing PV inverter on Input 1. I can’t remember what it showed earlier but fairly certain it wasn’t an inverter. This also shows 7kW.
Apart from this the system is still working as it should and when I check the MyEnergi app all values are pretty close to the ones shown on the Victron display, apart from this spurious 7kW.
Did a scheduled charge during the night and all looks good. This morning solar is charging battery and we are not consuming from grid so apart from this strange issue pretty pleased with the result of three months or so research, DNO applications, building battery and installation. Huge learning curve though!
Any suggestions as to what to look for next or what could be causing this? I'm not very familiar with Victron and this is my first foray into DIY battery storage.
Thanks in advance.
Over the past few months have been installing the following: Multiplus 2 48/5000, Seplos 280Ah battery, Venus OS running on Raspberry Pi with display. 230v is connected to AC In, ESS enabled with CT clamp connected to the 3.5mm plug in inverter to monitor grid.. These are installed in garage and connected to a consumer unit in garage. This is in addition to a seperate Solaredge PV system that was installed last year. I will eventually fit a current sensor to the Solar PV output to show PV but that'll be in the future.
Fired the whole thing up yesterday morning and all was working as expected. Battery charging when producing excess solar and then supplying house load when insufficient solar. Charged car from battery at 3kW to check for any cables or connections getting hot. All ok.
During the afternoon I inadvertently touched the main breaker test button in the consumer unit and everything shut down. Switched everything back on and now for some reason the display is showing a PV Inverter connected with around 7kW and the Grid is now showing -7kW. Reset everything and have went through all the settings to see if anything had changed. In the device list it is showing PV inverter on Input 1. I can’t remember what it showed earlier but fairly certain it wasn’t an inverter. This also shows 7kW.
Apart from this the system is still working as it should and when I check the MyEnergi app all values are pretty close to the ones shown on the Victron display, apart from this spurious 7kW.
Did a scheduled charge during the night and all looks good. This morning solar is charging battery and we are not consuming from grid so apart from this strange issue pretty pleased with the result of three months or so research, DNO applications, building battery and installation. Huge learning curve though!
Any suggestions as to what to look for next or what could be causing this? I'm not very familiar with Victron and this is my first foray into DIY battery storage.
Thanks in advance.