Well, today's job started to go wrong quite early and just got worse as the day continued..
I'm meant to be replacing a shower, installing an extractor fan and replacing a light fitting...
1. The board is an old wooden frame wylex
2. The equpotential bonding is old imperial approx =4mm and none on gas
3.The existing shower circuit also supplies the boiler and a socket in the kitchen
4.The lighting circuit CPC had rotted at the board
5.The socket circuit CPCs had rotted at the board
6.There's a double oven.... I don't know if there's a cooker circuit
Appart from the bathroom all the other rooms have been decorated and the carpets cleaned,,, the owners really didn't want me to go in any of the other rooms... I told them I have to!
Oh ... and the mains is in the attached garage which doesn't meet the soffit board and has a flat roof
I've also determined that the cables are copper clad aluminiym, thankfully I can get to them,,, the lights up through the cavity and the socket cct under the floor of the room that backs onto the garage
I'm meant to be replacing a shower, installing an extractor fan and replacing a light fitting...
1. The board is an old wooden frame wylex
2. The equpotential bonding is old imperial approx =4mm and none on gas
3.The existing shower circuit also supplies the boiler and a socket in the kitchen
4.The lighting circuit CPC had rotted at the board
5.The socket circuit CPCs had rotted at the board
6.There's a double oven.... I don't know if there's a cooker circuit
Appart from the bathroom all the other rooms have been decorated and the carpets cleaned,,, the owners really didn't want me to go in any of the other rooms... I told them I have to!
Oh ... and the mains is in the attached garage which doesn't meet the soffit board and has a flat roof
I've also determined that the cables are copper clad aluminiym, thankfully I can get to them,,, the lights up through the cavity and the socket cct under the floor of the room that backs onto the garage