I beg to differ - with a T & E installation, the higher reading will be at the switch, as the CSA of the CPC is smaller than that of the 'Line' conductor.I use a 1552.If you just want to check there is earth continuity at switches, connect a wander to the MET and probe to the screw heads.
Max R1+R2 (or max Zs if you prefer) will always be at the light, not the switch.
You may be losing the length of the 'run' of the 'switched live' to the light fitting, but you gain the same length in CPC, which is a higher resistance, so a higher Zs.