Odd psc
micky j.c.
Jan 28, 2010
6
Hi Guys,
I have ben changing a C/U for a client and whilst performing my Ze/PFC/PSC tests I obtained the following results using my Fluke 1652 multitester
The installation is a TT I have just installed a new spike and did not test the old one before I removed it so I have no reference
Ze L - Pe = 4.7ohms @ 56A PFC
Ze L-N = 25.6ohms @ 51A PSC
Should I be worried by these results
Mike
Exactly why i am asking the forum for info as usually PSC would be better than PFC on a TT system
Hi Guys,I have ben changing a C/U for a client and whilst performing my Ze/PFC/PSC tests I obtained the following results using my Fluke 1652 multitester
Mike
something seriously wrong with L-N loop. how exactly did you measure it?
Even Money, dodgy meter
2/1 User error
33/1 Supply fault
Hi guys
and the answer is........... the rod!
I dont know why but its the only answer i can give. My Dad was performin the test and he Knows what he is doing, properly calibrated Fluke 1652.
I called E-on they came out next day measured just L-N as its a TT system and got 0.12ohms @ 10 KA whilst he was there anyway I asked him nicely to supply an earth so he installed a Sheath (TN-S) earth for free but wouldn't hook up my new tails to the meter and get rid of the old earth leakage trip:O saying not wanting to be a jobsworth but thats ur electric suppliers department n left me too it.
So with a nice new sheath earth I am obtaining brilliant results ( L-PE 0.21omhs @ 1.2KA - L-N 0.01ohms @ 10KA). I may use that one in the future if i cant get a good spike on a TT system again thus avoiding paying for a PME( i know a sheath ain quite as good but its loads better than a spike)
I did test the Ze of the spike again out of curiousity just L-PE this time it was 41ohms @ 7Amps.
Hi guysand the answer is........... the rod!
Out of interest how do they connect the earth wire to the sheath.
Why do you say this? IMHO rod is safest of all as any faults on DNO's network will not cause you to loose your Earth unlike on TN systems.
Also when you say 'paying for PME' does that mean you pay the DNO to convert their network (or at least the part you are using) to PME and are then able to present you with a TN-C-S earth?