Basically.....
Student let upstairs flat with 5 bedrooms, living room, kitchen, 1x8.5kw shower.....various fans in toilets TV's in most rooms etc to give you an idea of current demand.
TN-S earthing arrangement.
WYLEX 10 way board, 5x 6A circuits, 2x20A radials, 1x32A Ring, 1x32A Shower, 1x spare. Single RCD 63A 30mA for latter circuits.
Ze = 0.13 Very good imo!! Double checked approx 10 times as the head looked like TNC-S but proved it wasn't.
This is where it got sticky for me........I'm awaiting a response from NAPIT technical about this also.
DB is fed via SWA 16mm 2 core.
LIVE conductor is one of the 16mm cores
EARTH conductor is one of the 16mm cores
NEUTRAL "conductor" has been made up of 7x 1.5mm PVC singles in black!
Now I know that the 16mm LIVE will take approx 80A using the reference method etc but what do you guys think of the NEUTRAL setup?
1.5mm using the same reference method can take a maximum of 20A so in parallel they could potentially take approx 7x20A = 140A which would be sufficient?
I just don't like the setup at all.
This is the second 5 year PIR on the property and there has never been any problems in approximately 10 years etc.....the previous PIR was carried out by Cityworks @ Newcastle Council who passed it 5 years ago.
Give me your opinions please as i'm tempted to advise changing them to a 16mm Neutral but the landlord is saying the obvious "Its been alright for over 10 years" etc etc
Still awaiting callback from NAPIT also bad day explode
cheers
Student let upstairs flat with 5 bedrooms, living room, kitchen, 1x8.5kw shower.....various fans in toilets TV's in most rooms etc to give you an idea of current demand.
TN-S earthing arrangement.
WYLEX 10 way board, 5x 6A circuits, 2x20A radials, 1x32A Ring, 1x32A Shower, 1x spare. Single RCD 63A 30mA for latter circuits.
Ze = 0.13 Very good imo!! Double checked approx 10 times as the head looked like TNC-S but proved it wasn't.
This is where it got sticky for me........I'm awaiting a response from NAPIT technical about this also.
DB is fed via SWA 16mm 2 core.
LIVE conductor is one of the 16mm cores
EARTH conductor is one of the 16mm cores
NEUTRAL "conductor" has been made up of 7x 1.5mm PVC singles in black!
Now I know that the 16mm LIVE will take approx 80A using the reference method etc but what do you guys think of the NEUTRAL setup?
1.5mm using the same reference method can take a maximum of 20A so in parallel they could potentially take approx 7x20A = 140A which would be sufficient?
I just don't like the setup at all.
This is the second 5 year PIR on the property and there has never been any problems in approximately 10 years etc.....the previous PIR was carried out by Cityworks @ Newcastle Council who passed it 5 years ago.
Give me your opinions please as i'm tempted to advise changing them to a 16mm Neutral but the landlord is saying the obvious "Its been alright for over 10 years" etc etc
Still awaiting callback from NAPIT also bad day explode
cheers