Did a PIR on a 3 bed semi requested after diy socket move resulted in burnt cables in kitchen behind tiles,,
repaired it and recommend the PIR
put an estimate in and they were shocked ... here it is
upgrade consumer unit ,,,, recessed at the moment may need to surface mount which would require extending cables
upgrade main earth and bonding (short easy runs)
Combi boiler radial no r1+r2 investigate/repair
Outbuilding spur to fuse correctly at ring point
broken cpc on upstairs lighting,,,investigate repair
Kitchen light no r1+r2
investigate ring cct 4mm on one side 2.5mm on other leaving cu. readings indicates spurs/bridges etc
Replace worn metal sockets
Replace metal light switches where no cpc available on switch drop