Good evening all, I have had a very eventful day and I would like to share it with you's and see what you's think.
Went to a house this morning to fit a cooker hood, oven, hob and a light in a kitchen every thing in done and ok. So went to leave and the decorator had said that when he was wetting the wall to take the wallpaper off he got a shock from the plasterboard, so started the usual testing any screws nails etc that I could see and found that all screws are at 230ish volts:O
Continued my investigation to find that this is a metal framed, then plasterboard screwed on wall.
My findings were that when testing for voltage throgh the circuit conductor and the metal stud I got about 45volts and through the live circuit conductor and the metal stud wall I was getting about 190volts ( circuit is rcd protected ).
My thinking is that the stud framing is not earthed and that the cable has been jammed or screw through, and with the framimg not being earthed that the rcd has not tripped.
The breaker for the socket circuit that when turned on and giving me the voltage has been turned off and the client has been informed about the problem but they seem they just want to carry on as before.
Has anyone had this before and any help would be great thanks
Went to a house this morning to fit a cooker hood, oven, hob and a light in a kitchen every thing in done and ok. So went to leave and the decorator had said that when he was wetting the wall to take the wallpaper off he got a shock from the plasterboard, so started the usual testing any screws nails etc that I could see and found that all screws are at 230ish volts:O
Continued my investigation to find that this is a metal framed, then plasterboard screwed on wall.
My findings were that when testing for voltage throgh the circuit conductor and the metal stud I got about 45volts and through the live circuit conductor and the metal stud wall I was getting about 190volts ( circuit is rcd protected ).
My thinking is that the stud framing is not earthed and that the cable has been jammed or screw through, and with the framimg not being earthed that the rcd has not tripped.
The breaker for the socket circuit that when turned on and giving me the voltage has been turned off and the client has been informed about the problem but they seem they just want to carry on as before.
Has anyone had this before and any help would be great thanks