I have a customer that want's a shed supply fitted. Cable was installed when patio was installed 8 years ago. Cut end of cable left unterminated and open to elements. Before I quoted I decided to test the cable. I cut off 30cm of cable before strpping.
I found poor IR results:
Core 1 & Core 2 = > 299 MOhms
Core 2 & Core 3 = > 299 MOhms
Core 1 & Core 3 = 2.7 MOhms
Core 3 & Armour = 0.5 MOhms
Core 1 & Armour = > 299 MOhms
Core 2 & Armour = > 299 MOhms
Could this just be water penetration via cut end or does it sound like more mechanical cable damage?
Should I cut another metre off the cable and try again or put a load on it to see if it "dries off"? Any suggestions.