power for smoke and heat detectors

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

matt.leung

Well-known member
Joined
Feb 26, 2009
Messages
1,062
Reaction score
0
Location
Bromley, Kent
do smoke alarms and heat detectors need to be wired into an RCBO? as this is what i have been told, as i wish to take it from the lighting circuit.

The smoke alarm and heat detector will be mains operated with battery backup, this is for a domestic re-wire.

 
They do need to be on an RCD protected cct (though don`t believe everything you see/read in B&Q!) ; as Zee has said, take `em from the lighting cct if that has RCD cover - if not, change the MCB to an RCBo.

The issue with putting them on a standalone RCBo is that it could trip, and no-one notice. If its a lighting cct, someone would realise that the lights weren`t working.

NB this info is only good for domestic (grade D) alarm installs. If you get into 5839-1, you have to do things differently.

KME

 
Why do they need to be on an RCD protected circuit?
its the burid cable that needs rcd, unless >50 deep or earthed armor

 
Why do they need to be on an RCD protected circuit?
Because of the bloody stupid change in the regs with the 17 th Ed. Cables buried 10 feet in the wall and covered by steel armoured plate 1" thick are OK .

This sudden obsession with drilling holes in cables has compromised people's safety in a fire condition . As said in other posts , if an RCD or MCB trips no one will notice that the Alarms are not powered.

If it was up to me they would be on a HRC fuse ,sealed like the main cut-out.

 
Not sure if this relevant about putting them on a local lighting circuit but was called out to a property last week. Builders electrician had fitted two screwfix mains smokes three years before. They had been playing up beeping in the night. I changed batteries but called out again still doing it. Went around this evening lady said she wanted them taking out altogether so talked her into having two EI141 smokes now hoping they are going to be ok. Not sure what problem could be but she has low energy lamp in pendant feeding smokes. I always put seperate circuit in for smokes not happy running them of lighting circuit. if you read instructions smokes should not be put on circuit containing fluorescent lights and dimmers and there is a lot of other things you need to be aware of in instructions. I am happy to have them on a seperate circuit as the only time they would trip is if you have a short on cable but that is unlikely.

 
The issue with putting them on a standalone RCBo is that it could trip, and no-one notice. If its a lighting cct, someone would realise that the lights weren`t working.KME
What if it was the middle of the night, asleep with all lights out anyway, and there was a fire?

 
Which happens to be the spec. of a grade D system.

Otherwise, you could also use the reasoning that there might be a power failure, which would cause the smokes to become inoperative, during the period they`re most likely to be required - candles & oil lamps front & centre.....??

 